  • foot-candle measurement

    I have an oddball question. How can I measure a value of 5 foot-candles through a green lens in a room with a highbay fluorescent light 20 feet overhead? The fluorescents are 5000k color. This isn't really a photography question, but I figured someone here could help. What I'm up against is corporate safety nazis saying an exit sign isn't illuminated - but the bulbs are on. Thanks.
    God forgives, rocks don't
    -sons of thunder

  • #2
    You won't be able to. Exit signs don't put off that much light. From your description sound like your fluorescents are washing out the exit signs. How high are the exit signs?
    Check out .

    Comment


    • #3
      Here is the code. See if any of the exceptions apply to you or have the mfr. send you info on your signs.


      SECTION 1011
      EXIT SIGNS
      1011.1 Where required. Exits and exit access doors shall be
      marked by an approved exit sign readily visible from any direction
      of egress travel. The path of egress travel to exits and
      within exits shall be marked by readily visible exit signs to
      clearly indicate the direction of egress travel in cases where the
      exit or the path of egress travel is not immediately visible to the
      occupants. Intervening means of egress doors within exits shall
      2010 CALIFORNIA BUILDING CODE
      be marked by exit signs. Exit sign placement shall be such that
      no point in an exit access corridor or exit passageway is more
      than 100 feet (30480 mm) or the listed viewing distance for the
      sign, whichever is less, from the nearest visible exit sign.
      Exceptions:
      1. Exit signs are not required in rooms or areas that
      require only one exit or exit access.
      2. Main exterior exit doors or gates that are obviously
      and clearly identifiable as exits need not have exit
      signs where approved by the building official.
      3. Exit signs are not required in occupancies in Group U
      and individual sleeping units or dwelling units in
      Group R-1, R-2, R-3 or R-3.1.
      4. Exit signs are not required where inmates are housed,
      or held in dayrooms, sleeping rooms or dormitories in
      occupancies in Group 1-3.
      5. In occupancies in Groups A-4 and A-5, exit signs are
      not required on the seating side of vomitories or openings
      into seating areas where exit signs are provided in
      the concourse that are readily apparent from the
      vomitories. Egress lighting is provided to identify
      each vomitory or opening within the seating area in an
      emergency.
      1011.2 Dlumination. Exit signs shall be internally or externally
      illuminated.
      Exception: Tactile signs required by Section 1011.3 need
      not be provided with illumination.
      > 1011.3 Tactile exit signs. For the purposes of Section 1011.3,
      the term "tactile exit signs" shall mean those required signs
      that comply with Section 1117B.5.1 Item 1. Tactile exit signs
      shall be required at the following locations:
      1. Each grade-level exterior exit door shall be identified by
      a tactile exit sign with the word, "EXIT."
      2. Each exit door that leads directly to a grade-level exterior
      exit by means of a stairway or ramp shall be identified
      by a tactile exit sign with the following words as
      appropriate: .
      A. "EXIT STAIR DOWN"
      B. "EXIT RAMP DOWN"
      C. "EXIT STAIR UP"
      D. "EXIT RAMP UP"
      3. Each exit door that leads directly to a grade-level exterior
      exit by means of an exit enc?osure that does not utilize
      a stair or ramp, or an exit passageway shall be
      identified by a tactile exit sign with the words, "EXIT
      ROUTE."
      4. Each exit access door from an interior room or area that
      is required to have a visual exit sign, shall be identified
      by a tactile exit sign with the words, "EXIT ROUTE."
      5. Each exit door through a horizontal exit shall be identified
      by a tactile exit sign with the words, "TO EXIT. "
      2010 CALIFORNIA BUILDING CODE
      MEANS OF EGRESS
      1011.4 Internally illuminated exit signs. Electrically powered,
      self-luminous and photoluminescent exit signs shall be
      listed and labeled in accordance with UL 924 and shall be
      installed in accordance with the manufacturer's instructions
      and Chapter 27. Exit signs shall be illuminated at all times.
      1011.5 Externally illuminated exit signs. Externally illuminated
      exit signs shall comply with Sections 1011.5.1 through
      1011.5.3.
      1011.5.1 Graphics. Every exit sign and directional exit sign
      shall have plainly legible letters not less than 6 inches (152
      mm) high with the principal strokes of the letters not less
      than 3/4 inch (19.1 mm) wide. The word "EXIT" shall have
      letters having a width not less than 2 inches (51 mm) wide,
      except the letter "I," and the minimum spacing between
      letters shall not be less than 3/8 inch (9.5 mm). Signs larger
      than the minimum established in this section shall have
      letter widths, strokes and spacing in proportion to their
      height.
      The word "EXIT" shall be in high contrast with the background
      and shall be clearly discernible when the means of
      exit sign illumination is or is not energized. If a chevron
      directional indicator is provided as part of the exit sign, the
      construction shall be such that the direction of the chevron
      directional indicator cannot be readily changed.
      1011.5.2 Exit sign illumination. The face of an exit sign
      illuminated from an external source shall have an intensity
      of not less than 5 foot-candles (54 lux).
      1011.5.3 Power source. Exit signs shall be illuminated at all
      times. To ensure continued illumination for a duration of not
      less than 90 minutes in case of primary power loss, the sign
      illumination means shall be connected to an emergency
      power system provided from storage batteries, unit equipment
      or an on-site generator. The installation of the emergency
      power system shall be in accordance with Chapter 27.
      Exception: Approved exit sign illumination means that
      provide continuous illumination independent of external
      power sources for a duration of not less than 90 minutes,
      in case of primary power loss, are not required to be connected
      to an emergency electrical system.
      1011.6 Floor-level exit signs. Where exit signs are required by
      Chapter 10, additional approved low-level exit signs which are
      internally or externally illuminated photoluminescent or
      self-luminous, shall be provided in all interior corridors of
      Group A, E, I and R-2.1 occupancies and in all interior rated II
      exit corridors serving guest rooms of hotels in Group R, Division
      1 occupancies.
      Exceptions:
      1. Group A occupancies that are protected throughout
      by an approved supervised fire sprinkler system.
      2. Group E occupancies where direct exits have been
      provided from each classroom.
      3. Group I and R-2.1 occupancies which are provided
      with smoke barriers constructed in accordance with
      Section 407.4
      4. Group 1-3 occupancies.
      345
      II
      MEANS OF EGRESS
      The bottom of the sign shall not be less than 6 inches (152
      mm) or more than 8 inches (203 mm) above the floor level and
      shall indicate the path of exit travel. For exit and exit-access
      doors, the sign shall be on the door or adjacent to the door with
      the closest edge of the sign or marker within 4 inches (102 mm)
      of the door frame.
      Note: Pursuant to Health and Safety Code Section 13143,
      this California amendment applies to all newly constructed
      buildings or structures subject to this section for which a
      building permit is issued (or construction commenced,
      where no building permit is issued) on or after January 1,
      1989.
      1011.7 Path marking. When exit signs are required by Chapter
      10, in addition to approved floor-level exit signs, approved
      path marking shall be installed at floor level or no higher than
      8 inches (203 mm) above thefloor level in all interior rated exit
      corridors of unsprinklered Group A occupancies, and Group
      R-1 and R-2 occupancies.
      Such marking shall be continuous except as interrupted by
      door-ways, corridors or other such architectural features in
      order to provide a visible delineation along the path of travel.
      Note: Pursuant to Health and Safety Code Section 13143,
      the California amendments of this section shall apply to all
      newly constructed buildings or structures subject to this
      section for which a building permit is issued (or construction
      commenced, where no building permit is issued) on or
      after January 1, 1989.
      >>>>>>>>>>>>>>>>>>>>>>>>>>
      ERIK


      95 yj, locked lifted, and ready to rock!

      Comment


      • #4
        Thanks, my first reaction to my HR was to tell them to pull their heads out and it would be easier to see the light.
        God forgives, rocks don't
        -sons of thunder

        Comment


        • #5
          if you have a narrow spot meter, you could figure it out relative to other light intensities.
          [COLOR="#FF0000"]R[/COLOR]edneck [COLOR="#FF0000"]D[/COLOR]riveway [COLOR="#FF0000"]F[/COLOR]ab
          www.DanielBuck.net - www.DNSFAIL.com - www.FurnitureByBuck.com

          Comment


          • #6
            Nah, all I have are narrow-minded inspectors. I was just wondering if there was a way to ballpark this thing. Mostly it's a principal issue. I inspect them and repair them on a monthly basis. They came in for an annual audit, didn't like their foo-foo coffee or whatever and dinged us on our corporate review while trying to make it look like I haven't done my job. I get a little bitter about such things... I guess I'll just have to order all new lighting and put the inspector's name on the justification. Sorry, rant over.